ANSI/FCI 70-2 Control Valve Leakage

ANSI/FCI 70-2 Control Valve Leakage

ANSI/FCI 70-2 Control Valve Leakage

(OP)
When describing allowable leakage, the standard refers to ".01% of rated valve capacity". Rated valve capacity is defined as "the quantity of test fluid that would pass through the valve at rated travel under the stated pressure conditions as defined by the appropriate equations and manufacturers ratings."

This reads like something the government would come up with. We want to quantify allowable leakage for a metal/metal seated ball valve to meet Class IV. If I assume (yes, I know the repurcussions of that..) that "rated valve capacity" is Cv, then I can have .01% of Cv/min. and meet Class IV.

Can anyone help me with this one ? Gratitude is given in advance.

Joe   

RE: ANSI/FCI 70-2 Control Valve Leakage

Yes, that is how I've interpreted it also.

RE: ANSI/FCI 70-2 Control Valve Leakage

joeswoes,
        for me too, if not specified otherwise, "valve rated travel" means the valve 100% open.

        Just for information, I add that sometimes Customer specifications require FCI 70-2 tightness classes in conditions very different from the standard ones for which classes are defined (typically for cryogenic valves and then -196°C instead of room temperature and helium instead of air, etc.), without giving clear rules for the extension of the standard's scope...

        Please take also a look at Thread174-76111 and Thread408-76110 about the document in object.

Thanks and regards,           'NGL
   

RE: ANSI/FCI 70-2 Control Valve Leakage

FCI 70-2 specifies leakage rates on a test stand with when tested according to the FCI procedure (usually 50 psi air at ambient temperature)

The FCI leakage classes are a prety good indication of how carefully the valve parts were fitted together.

How much leakage will you get in service at, say, 450 degrees, steam, at 200 psi?  Anybody's guess.  Aside from the class V procedure which tests for leakage at service pressure, the ANSI classes are not directly related to the expected leakrate in service.  

Some valve types (pilot-balanced globe valves) shut off tighter at elevated differential pressures.  Other valve types (unbalanced globe) require additional actuator force proportional to diff. pressure.  Eccentric rotary valves may be installed with the flow tending to unseat the plug or with the flow tending to add additional seat load. Guess which one shuts off tighter.   And of course the odd bit of weld slag coming down the pipe three minutes after you commission the valve will tend to change everything anyway.   

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources