Induction Vs Synchronous motors for paper mill
Induction Vs Synchronous motors for paper mill
(OP)
What are the decision making advantages / disadvantages for choosing induction or synchronous motors for industrial applications such as paper mill refiners? The sizes are 1,000 to 3,000 HP, and the voltage is 2.4-kV.
The mill is served by a 33 MVA 115/12.47-kV transformer, and the expansion will require the installation of a second 33 MVA transformer and second 12.47-kV bus. The refiners are served through 12.47/2.4-kV stepdown transformers.
The mill is served by a 33 MVA 115/12.47-kV transformer, and the expansion will require the installation of a second 33 MVA transformer and second 12.47-kV bus. The refiners are served through 12.47/2.4-kV stepdown transformers.





RE: Induction Vs Synchronous motors for paper mill
There is a very detailed article on this subject on the GE website if you can find it.
imho, a great disadvantage of sync motors is they are more complex ==>> more stuff to maintain and more stuff which can fail.
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: Induction Vs Synchronous motors for paper mill
http://ww
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: Induction Vs Synchronous motors for paper mill
RE: Induction Vs Synchronous motors for paper mill
I believe low-speed synchronous motors will provide a signficantly higher efficiency than an equivalent induction motor, or at least that used to be true. If speed is 720 rpm or higher, I don't think there is much difference in efficiency.
The ability of the synchronous motors to operate at a leading power factor to provide vars to your system is also another advantage.
RE: Induction Vs Synchronous motors for paper mill
Typical average efficiencies and then kWH consumptions in one year are:
Induction Motor (EFF =93.8);
kWH= (1000 * .746 / 0.938 )*365*24 = 6,966,908
Synch. @0.8 PF (EFF=94.2);
kWH= (1000*.746/0.942)*365*24 =6,937,325
Synch. @1.0PF (EFF=95.1);
kWH= (1000*.746/0.951)*365*24 =6,871,672
Assuming energy cost $0.05 dollars per kWH, the yearly electric bill becomes:
Induction ---------- $348,345
Synch @ .8PF-------$346,866
Synch @1PF -------$343,583
RE: Induction Vs Synchronous motors for paper mill
In some territories, there could be an additional pf penalty in one form or another that could significantly boost the cost advantage.