This is a stupid question, but how are cable ratings established?  Is it based on the thickness of insulation or cable gauge size?  

Does a 4kV rated cable mean 4kV peak voltage?  So can it actually take on 8kV of peak to peak voltage?

thanks

RE: cable rating

The current-carrying capacity of insulated cable is based on keeping the insulation temperature below its rated maximum.  So both the insulation and the wire size are factors.  

Cable voltage ratings are typically ac rms values.  

RE: cable rating

QUESTION 1: Does a 4kV rated cable mean 4kV peak voltage?  In the ANSI marketplaces, the selection of the cable insulation level to be used in a particular installation shall be made on the basis of the applicable phase to phase voltage and overvoltage duration indirectly considered in the minimum standard insulation thickness of 100%, 133% or even 173% in accordance with ICEA/NEMA, AEIC and other standards.

QUESTION 2:...So can it actually take on 8kV of peak to peak voltage?

There are cable with dual rating such as 5 kV with 133% insulation for ungrounded system and 8 kV with 100% insulation for grounded system as shown in the enclose link.

http://www.okonite.com/Product_Catalog/section2/sheet4.html.

RE: cable rating

4kV typically means the insulation is rated for 4kV RMS AC. Peak-to-peak is 2 * sqrt(2) * Vrms (for sinusoidal waveforms).

Voltages are typically given as phase-to-phase, assuming the system is solidly grounded. For system that are impedance grounded (where ground offsets occur only during faults), 133% rated insulation is usually specified. Many engineers also specify 133% for solidly grounded systems for a little safety factor. For ungrounded system, use 173%.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources