code requirement of pvc duct

code requirement of pvc duct

code requirement of pvc duct

(OP)
Can anyone help me with the code (united mechanical code and international code) limitation on the use of PVC duct? The PVC duct is used to supply conditioned air (not exhaut) and it is to be routed inside of the return plenum. The plenum is sprinkler protected.

RE: code requirement of pvc duct

You would probably have to verify the flame-spread rating of the PVC with the manufacturer.  There are types of PVC piping with a coating to improve the flame-spread rating to allow use in a return air plenum.  

RE: code requirement of pvc duct

This is what my spec reads:

A.  General requirements - Non-combustible materials, Class 1 (25 flame spread, 50 smoke developed), conforming to NFPA 90A, NFPA 90B, NFPA 91 and UL 181.

RE: code requirement of pvc duct

(OP)
Thanks, walkes and cme. Per my understanding, International Mechanical Code restricts the use of PVC ductwork/piping to be underground only. Similar to Uniform Mechanical Code, it requires plastic duct/piping in the return plenum to meet 25/50 requirement and there is no exception (it does not matter if the return plenum has srpinkler or not).

Please advise if anything above not accurate.

RE: code requirement of pvc duct

sfxf,

Harvel makes a CPVC that meets the 25/50 requirement of the IMC, (http://www.harvel.com/).  But 603.7.4 of the 2000 IMC does say that "Plastic duct and fittings shall be utilized in underground installations only," so I believe that you need to look at other materials.

What is your application that you would need to use PVC for supply air?

---KenRad

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources