UPS Ground Problem?

UPS Ground Problem?

UPS Ground Problem?

(OP)
A while back, a large process control room UPS (20kVA ferroresonant, continuous online, 1-phase 120V output) lost it's phase relationship and dropped out of synchronizm with the maintenance bypass frequency and began freewheeling.  

While freewheeling, all lighting and analog instruments in the control room began pulsating at the rate of phase difference between the utility frequency and UPS output frequency.

Is this indicative of improper/insufficient grounding for UPS/Bypass sources; or other unrelated phenomena?

RE: UPS Ground Problem?

Typically the output of the UPS is either inverter based or bypass based (open transition).  I'm not sure how the low would have seen "phase difference between the utility frequency and UPS output frequency".  The pulsating maybe a result in the inverter output being much lower than 60hz, causing flickering.  
A freewheeling inverter, should have transfered to bypass and supplied bypass power to the load.

RE: UPS Ground Problem?

Ferro UPS's commonly have an output transformer with separate primary windings for the AC (bypass) and inverter inputs. If a malfunction is causing the inverter to run at the same time the AC input is connected, the output voltage would be modulated (beat) at a frequency equal to the difference between the two sources.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources