determining minimum slope in pipe not flowing full
2

determining minimum slope in pipe not flowing full

determining minimum slope in pipe not flowing full

(OP)
I have one house that I am hooking up to a sanitary sewer main 200 feet away via an 8" HDPE pipe, therefore pipe not flowing full.  How do I calculate what pipe slope is necessary to flow successfully?

RE: determining minimum slope in pipe not flowing full

You are going to have to solve for slope at full flow, then determine partial flow velocity to be 2.5 fps or more, using the relationships and equations on pages 111-113 here:

http://164.156.71.80/VWRQ.asp?docid=2087d8407c0e00000000047c0000047c&context=2&backlink=WXOD.aspx%3ffs%3d0442d740780d00008000084d0000084d%26ft%3d1

Remember: The Chinese ideogram for “crisis” is comprised of the characters for “danger” and “opportunity.”
-Steve

RE: determining minimum slope in pipe not flowing full

1:50 is a good starting place.

RE: determining minimum slope in pipe not flowing full

You use the old standby meathod.....ITERATION!!

RE: determining minimum slope in pipe not flowing full

2
Are you using an 8" pipe for the service? unless you have a 5 bathroom house that is way over sized. cut back to a max of 6" and even check out a 4". the slope will be the diff. in elev. from the house outlet and the elevation of the main where you hook up divided by the 200 feet to the main. Has nothing to do with half full or full

RE: determining minimum slope in pipe not flowing full

The standard in my area is 6" Dia. pipe  at a slope of 1/8" per foot (these are minimums for size and slope).  This provides a flow capacity of 1.2 cfs and a velocity of 3.5 fps, flowing full, calculated with Manning's equation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources