Different voltage grade of cable on same cable tray

Different voltage grade of cable on same cable tray

Different voltage grade of cable on same cable tray

(OP)
We have two different cable groups, 600/1000V(U0/U) for Low Voltage Power and control and 150/250V for instrumentation. Power is Ac690V and 400V AC. Some power control cables (for dry contacts) are driven by AC110V and DC24V employed as 150/250V cables. In the case that those power control cables(150/250V grade) are laid together with 690V power cables on the same cable tray, I do not see any problem but is was raised by someone as per spec. The mentioned problem is that earth fault power cable by damage causes insulation grade of control cable(150/250V).
I'm not sure if this is problem in technical point view or this is specification problem only.
Anybody helps my difficulties, please ?

RE: Different voltage grade of cable on same cable tray

It doesn't sound like you're in the US, but here in US, this is acceptable provided all of the insulation is rated for the highest voltage in the tray.  If you have a 480V circuit in the tray, all cables must be insulated for at least 480V regardless of the actual voltage of the circuit.  

RE: Different voltage grade of cable on same cable tray

Thats interesting. I assume this is part of an NEC requirement. Do you know where off the top of your head this is talked about in the NEC? I have not been in this area long but was not aware of this requirement. Thanks.

RE: Different voltage grade of cable on same cable tray

buzzp, it is in NEC Art.300.3(C)(1).

RE: Different voltage grade of cable on same cable tray

(OP)
What about in Europe, in U.K.

RE: Different voltage grade of cable on same cable tray

I see that requirement is for voltages of 600V or less. The OP has voltages above this so what would the requirements in the US be for the case of 690V circuit in the same raceway as control power (120VAC)? In reading the next section of the NEC (300.3(C)(2), it looks as though this would be allowed (thinking of motor power and control power here). Is this true? Thanks.

RE: Different voltage grade of cable on same cable tray

buzzp,

Above 600V, the basic rule is that the lower voltage circuits must be physically isolated from the the high voltage circuit by a metal barrier and **cannot** occupy the same raceway.  Mixing would only be allowed for the narrow exceptions provided in 300.3(C)(2).  

Your example of motor control conductors and motor power conductors would generally NOT be allowed in the same conduit if the motor feeder was above 600V.  They can be in the same motor starter enclosure or within the same motor terminal box, but could not share a conduit or cable tray.  

This rule is fairly sacrosanct in the US, at least in my experience.  In fact many electricians insist that 480V and 120V circuit cannot be run in the same conduit, but this is incorrect as noted above.  

RE: Different voltage grade of cable on same cable tray

Ok, I understood that part correctly but failed to realize that circuits <600 had to have the same insulation rating if they are in the same raceway, conduit, etc.

Now maybe someone can answer the OP question concerning Europe.

RE: Different voltage grade of cable on same cable tray

(OP)
Thanks
You all helps me a lot.

RE: Different voltage grade of cable on same cable tray

(OP)
With regard to same insulated cables on the same cable tray, I needs to have any requirement in IEC/Europe. Anybody tells me.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources