how long can you legally run liquid tight
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: liquid tight coduit
Liquidtight Flexible Metallic Conduit (LFMC) has no maximum. Liquidtight Flexible Nonmetallic Conduit (LFNC) is limited to six feet.
Regards,
William
RE: liquid tight coduit
It also cannot be used "where subject to physical damage" and must be supported every 4.5 feet and within 12 inches of each termination, except as covered in the exceptions. This is Article 350 in the 2002 NEC. I don't know if this has changed in the 2005 NEC.
RE: liquid tight coduit
Sometime six feet of 4" sealtite dosen' give you the flex you need.
I have local inspectors grant a variance for longer runs of sealtite. You need to have a good reason.
RE: liquid tight coduit
John
RE: liquid tight coduit
William