Pen sized hole in PEX insulation at 36 kV

Pen sized hole in PEX insulation at 36 kV

Pen sized hole in PEX insulation at 36 kV

(OP)
This is way out of my field of work. Perhaps someone recognises the problem?

I visited a customer today to discuss replacement of old inverters with new ones. When we were finished the guy showed me some stumps of PEX cable where the insulation had failed and the resulting arc (impedance ground) had produced a neat perfectly circular hole with about 6 mm diameter (1/4 inch).

This has happened several times and all expertise say that these cables should withstand about 200 kV transients.

The switchgear is SF6 insulated and uses vacuum contactors. The load is a large furnace transformer for winning chromium fom chromium ore. The failures are not associated with swithing - they just happen.

Does this sound familiar? What could the reason be? Anyone seen this before? What did you do to prevent this failure?

RE: Pen sized hole in PEX insulation at 36 kV

As a general comment Cross linked polyethylene cables have been known to develop faults when exposed to high DC voltages. These faults do not show themselves until much later when the cable breaks down. Is it possible that the cables are being DC overpotential tested after installation?

RE: Pen sized hole in PEX insulation at 36 kV

(OP)
Thanks Powerful!

That is very possible. They are carrying 36 kV 50 Hz, but it is possible that they were tested with DC - in fact very probable - when installed and also during maintenance. I will ask the guys involved.

RE: Pen sized hole in PEX insulation at 36 kV


I am familiar with this problem. Most likely the pinholes are due to transisents. DC testing only ecourages a naturally occurring process which 'ages' the cable. I would need to know more in order to advise you further. How old are the cables? Do you have any surge protection on the system?...  
 
-cheers

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources