VT Fuse Failure-How to calculate?

VT Fuse Failure-How to calculate?

VT Fuse Failure-How to calculate?

(OP)
Hello all,

We have got an issue about a set of VTs.

A MV metal clad switchgear is supplied by a 13.8-4.16 kV Dyn1 power transformer. A set of PT (or VT) with the ratio 4.2 kV-120V is installed on the 4.16 kV STAR side to feed secondary line to line bus voltages for the metering and relay (ANSI # 27, 47, 59, 60) panel. The connection of the PT set is OPEN DELTA-OPEN DELTA corner grounded (commonly known as V-V grounded).

What will be the Line to Line voltages seen by the above mentioned relays on the 120 V side, and how to calculate them,

1)When one 13.8 kV phase is open due to a fuse blown condition of the primary side of the Dyn1 power transformer?
 
2)When one phase of the primary side of the VT is open due to VT primary side fuse blown condition?

3)When one phase of the secondary side of the VT is open due to VT secondary side fuse blown condition?

Most of the relay manuals (SEL, BASLER etc) discuss about the corresponding reflected voltages on the 120 V side with YNyn connected VT sets (e.g. generating stations where ANSI# 51V relays are fed).

Thanks in advance!

RE: VT Fuse Failure-How to calculate?

(OP)
PWR,

Thanks for your input.

I had already read BASLER technical paper brfore.

a)Table 11 of that paper gives the secondary voltages (pu)
  for the Dyn1 case.Is it possible to divide those by the
  ratio 35 to obtain the reflected secondary voltages on
  the 120 V side of the PT?

b)It does not show anything about case 3. My calculation
  shows it will be 0,1.0,1.0 pu.Is it correct?

Kiribanda

RE: VT Fuse Failure-How to calculate?

Table 11 will work directly.  Thus 0.5 pu is 60V on secondary or 2100V on primary.

Be cautious about the effect of the secondary load/burden.

Two weeks ago I was troubleshooting a situation with the blown VT primary fuse just like you described.  Because of the effect of what was connected on the secondary the phase voltages actually read: 120/67/138.

On your last example, if there is no secondary load connected you should see 1.0/0/0 pu.  The problem is, there always is something connected or you would not be concerned about what will happen!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources