Dual core CT(current tranformer) grounding 1 core ?

Dual core CT(current tranformer) grounding 1 core ?

Dual core CT(current tranformer) grounding 1 core ?

(OP)
Hi,

Due to a discussion at our workplace.
If only one of the dual cores are used on the secondary side of the measuring CT(MV-switchgear).

Is it better to short and ground the unused core or to just leave it open ?

Comments to drawbacks and benefits ?

RE: Dual core CT(current tranformer) grounding 1 core ?

There is no option. You must short the unused core and it's best to ground it as well. It will not influence the accuracy of the other core.

Leaving a CT open-circuited is NEVER an option, due to the chance for high-voltage and ultimately damage to the CT, personnel, other equipment, or all of the above.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources