Under reaching Zone 1 of Distance relays

Under reaching Zone 1 of Distance relays

Under reaching Zone 1 of Distance relays

(OP)
Generally speaking the zone 1 of distance relays is intentionally set to under reach the line length to the tune of 70 to 90 %. Also we know that the under reaching zone 1 is likely to over reach in case the parallel line is out of service and earthed. I invite reders your comments on ways to over come this quandary.
Regards

RE: Under reaching Zone 1 of Distance relays

almost all the major relay manufacturers have technical literature on their websites that discuss problems like this.

Bung
Life is non-linear...

RE: Under reaching Zone 1 of Distance relays

That's why relays have multiple settings groups.  One group is two lines in service, another is one line in service with the other open, a third setting group would be one in service and the other grounded.  The proper control system scheme will then switch between settings groups as needed.

RE: Under reaching Zone 1 of Distance relays

If I well understand your question, you can have a look to Walter A. Elmore, "Zero-sequence mutual effects on ground distance relays and fault locators", 46th Annual Protective Relaying Conference at the Georgia Institute of Technology, Atlanta, Georgia, April 29-May 1, 1992.

RE: Under reaching Zone 1 of Distance relays

(OP)
Sanalv,
Could you send me  a link to this paper ?
Thanks

RE: Under reaching Zone 1 of Distance relays

Sorry HiSet.

I have read some technical documents that reference the paper, I have been looking for it on the Net with no luck at all, up to date.

RE: Under reaching Zone 1 of Distance relays

Take a look at this instruction manual. There are six setpoint groups (bottom of page 2). Each setpoint group is a complete set of relay settings. The active group is selected by a control input signal.

http://www.selinc.com/datasheets/321ds.pdf

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources