Going from a Class I Div 1 to Class I Div 2 with MCHL Cable

Going from a Class I Div 1 to Class I Div 2 with MCHL Cable

Going from a Class I Div 1 to Class I Div 2 with MCHL Cable

(OP)
Is there a requirement to seal an MC-HL cable (MC cable that is approved for Class I Div 1 use) at the Div 1 and Div 2 boundry? Is so, how is that accomplished?

Thanks,
john0109

RE: Going from a Class I Div 1 to Class I Div 2 with MCHL Cable

Check NEC 501-5(d).

William

RE: Going from a Class I Div 1 to Class I Div 2 with MCHL Cable

Seal cable at both ends if routing through a hazardous area boundry.

RE: Going from a Class I Div 1 to Class I Div 2 with MCHL Cable

Seal the cable at the hazardous/nonhazardous boundary and within 450 mm of the enclosure.

William

RE: Going from a Class I Div 1 to Class I Div 2 with MCHL Cable

There is no boundary seal required for MC-HL.  Only the termination in Division 1 requires sealing.

RE: Going from a Class I Div 1 to Class I Div 2 with MCHL Cable

(OP)
Thanks for the replies. Is there a reference somewhere in the Code that states that MC-HL cable does not have to be sealed at the boundry?

RE: Going from a Class I Div 1 to Class I Div 2 with MCHL Cable

It is indirect. You have to look at the scope of each subsection of 501.4(D)

Section 501.4 (D)(1) states all cables are to be sealed at their terminations.
Sections 501.4 (D)(2) and (3) are for cables “in conduits.”

Type MC-HL and MI are the only “open” cable wiring methods permitted in Division 1. Both are required to be sealed at their terminations. generally, neither of them are in conduits at the boundary so neither of them are required to be sealed there.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources