Transformer specifications
Can someone tell me if there is a reference that provides typical distribution transformer impedances? I'm looking for %Z and either X/R ratios or %X and %R values.
The X/R table in IEEE red book is not adequate.
RE: Transformer specifications
The Navy has some tables at
http://www.ccb.org/docs/NAVGRAPH/16272.pdf
Tables PM-1, 2, and 3 are for the energy cost per kWh of x<$.04, .04<x<$.08, and x>$.08 respectively.
Let me know if that helps.
William
This is exactly what I have been searching. I was looking through the rest of the document and have a question. Table 17 lists cable resistance and reactance in magnetic and non-magnetic conduit. Are cable resistance and reactance for direct buried cable the same as the non-magnetic conduit values? If not where can I find some values for direct buried?
The NAVGraph document will also be useful to me since it has transformer losses. Thanks William!
You can think of the "non-magnetic conduit" values as being "not in magnetic conduit" values.  Once the conductors are no longer enclosed in a magnetic container, what is around the conductors has much less impact on impedance than does the relative location of the conductors.