Is the absorbed power of a motor equal to the driven load brake horsepower?
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: MOTOR ABSORBED POWER
The excess of power requirements are the motor losses developed due to the currents circulating in the rotor and stator windings, The friction and windage, the magnetic losses in the laminations and structural frame.
The factor that measures the input power is the motor efficiency (EFF) normally in percent.
EFF = (HPshaft output / HPinput) x 100
RE: MOTOR ABSORBED POWER
RE: MOTOR ABSORBED POWER
Is it :
bKW of load/motor eff
or
((1-eff) x rated motor kw)+ bKW of load
RE: MOTOR ABSORBED POWER
Note that the "rated motor kw" is always the shaft power (i.e. the motor output power, not the motor input power).
The motor losses are given by:
motor absorbed power - shaft power
= (1-eff) x motor absorbed power.
RE: MOTOR ABSORBED POWER
Your second expression is not correct.
IEEE STD 112 defines efficiency:
Efficiency is the ratio of output power to total input power. Output power is equal to input power minus the losses. Therefore, if two of the three variables (output, input, losses) are known, the efficiency can be determined by one off the following equations:
EFF= output power/input power
EFF= (input power – losses)/input power
EFF= output power/ (output power + losses)
Use the formula that better fits your available data.
You have named the input power as “absorbed power” and the output power as “bKW of load”
Note that the rated or Nameplate kW or HP apply only when the load connected to the shaft matches exactly the name plate power. It is obvious that the units must be consistent, kW or HP.