difreence between earth fault an short circuit level

difreence between earth fault an short circuit level

difreence between earth fault an short circuit level

(OP)
what is the difrence between short circut level and earth fault in electrical system, i can calculate SC level in a system,but how can i calculate erath fualt level??
 

regards ,

RE: difreence between earth fault an short circuit level

an 'earth fault' is just a special case of 'short circuit'.  A short circuit can be phase - neutral, phas e- phase, phase - phase to neutral etc - any combination of the 3 phases (and neutral where there is one).  Neutral and earth may or may not be the same thing.

Bung
Life is non-linear...

RE: difreence between earth fault an short circuit level

(OP)
for example in my project SC level of main busbar 33Kv is 31.5 KA and earth fault level is 450 A??!!! I have confused!

RE: difreence between earth fault an short circuit level

As Bung suggested, neutral and earth may not be connected directly. Low earth fault current occurs if the system neutral is connected to earth through a high impedance. Is this the case for your system?

RE: difreence between earth fault an short circuit level

(OP)
Tanks alehman
yes,in my case an impedance exist. but what is the advantage of using this ampedance ?
and you mean for reaching to 450A i should 31.5KA/R ???

RE: difreence between earth fault an short circuit level

The impedance is usually installed to reduce damage when an earth fault occurs. I=V/Z. Neglecting the impedance of your circuit and the source, Zg = 33,000 / sqrt(3) / 450.

If this is a real system, perhaps you should consult a licensed engineer to perform this analysis correctly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources