earth fault level

earth fault level

earth fault level

(OP)
one plant description :
4 gtg 42 MW(11/33 transformer)
sc level 31.5 KA
load 100 MVA
 
-we have big motor 11 kv 7MW , with transformer 10MVA  33/11 delta /star and earth fault 30A( star point to earth with resistance)
 -for 6KV taransformer earth fault is 50A( star point to earth with resistance)
 -for 400 v star point is solidly earth.

i want  to know how can i calculate erath fault level in transformer 11/33 ., in fact ? current (star point to earth)??




























RE: earth fault level

Simple calculation for earth fault current on 11kV side of 33/11kV unit transformer is [(11kV/Root3)/ Neutral earthing resistor value in Ohms].

RE: earth fault level

(OP)
but i have earthing fualt level in 11 kv side(30a), and i want to calculate this at 33 kv side 11/33kv conected to main busbar????

RE: earth fault level

A single phase to earth fault current of 1 p.u. on wye side of the transfomer show up as 0.58 p.u in the other two phases (lines) of the delta side and 0 in the one phase corresponding to one that is faulted on the secondary side.

Refer to some literature of S&C MV fuse applications. You may want to search the web or S&C publications. There must be other references too like IEEE buff book.

RE: earth fault level

RETURN SHOULD BE IN NUT, NOT EARTH.
EARTH SHOULD HAVE SAME FAULT CURRENT AS HOUSEHOLD.
IF I REMEMBER THIS IS .002 TO .006 AMPS, PER USER
OR, PER OUTLET OR STRING, AND
IS CONTROLED IN GOV SAFETY MANDATES,(US).
EARTH IS ALWAYS USED FOR SAFETY GROUND
AND NEVER USED FOR POWER.
EUROPE IS BECOMING MORE RESTRICTIVE,
THE OTHER COUNTRIES DO NOT SEEM TO CARE.
ELECTRIC SUPPLIERS MUST HAVE THEIR SPECIFIC
RULES AND REGULATIOMS FOR SOURCING POWER.
FOR USERS IN THE US THE CURRENT SHOULD
BE BELOW THE LEVAL THAT WILL KILL YOU.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources