Gentlemen (and ladies),

Is there a rule of thumb for approximating the triplen harmonics which are produced by IT and other equipment which would assist in calculating transformer size during the design process ?

In the UK the normal power system within a commercial building will comprise a three phase star connected system split down into 3 single phase services.

Too often it emerges that the transformer is underratted or the neutral conductor is overheating due to triplen harmonics from light fittings, computers, servers, UPS etc.

Is there any guidance for the designer published to allow him to make the necessary allowances ?    

RE: Determination of harmonics during design process

Many manufacturers of k factor rated transformers suggest various k factor ratings dependent on the percentage of connected non-linear load as compared to full load. For example, the following is from the Ge industrial website
"For commercial applications with significance nonlinear electronic loading, use K=4 for systems with 50% connected nonlinear electronic loads; K=13 for systems with 100% connected nonlinear electronic loads."

RE: Determination of harmonics during design process

Colinjohnson

Maybe not really related to your question, but check also the guide to the application of Engineering Recommendation G5/4 - In the assessment of harmonic voltage distortion and connection of non-linear equipment to the electricity supply system in the UK.

http://194.130.244.127/EnergyCentre/downloads/G5_4%20Installation%20Guidelines%20(EA).pdf

and also
http://www.lenze.co.uk/multimedia/HARM2002.pdf

for additional info

Regards
Ralph

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources