how to seal a high pressure line for hydro

how to seal a high pressure line for hydro

how to seal a high pressure line for hydro

(OP)
Had lots of tube repairs done so time to do a hydro, only isue is boiler stop valves were taken for repair and not returned yet.  Now return is delayed another week, but need to hydro to release contractors and continue with re-gunnite and re-insulation.  HELP!  Is there any way to use some sort of inflatable bladder to hold the line, 8" line to about 900 psi.  Has anyone done this with success or have another idea of how to accomplish hydro???????????

RE: how to seal a high pressure line for hydro

Sounds scary to me, you might end up with a water cannon. Good luck.

RE: how to seal a high pressure line for hydro

You might want to give these people a call.

http://www.expansionseal.com/html/hypg1.htm  


Come back with more information as to the line material and size.  
Is this weld end valve?

RE: how to seal a high pressure line for hydro

If Expansion Seal can’t fill your needs you want to check these people out as they rent high pressure test plugs.  They also rent all Classes and sizes of  blind flanges.

http://www.usaindustries.com/pipe_isolation_testing.htm

RE: how to seal a high pressure line for hydro

Why do you even need to perform a hydrotest? I would perform a pressure test (air squeeze at 25 lbs or use treated water at lower pressure - 300lbs) using one of the pipe sealing methods mentioned above to make a quick check for leaks. Your objective is not to proof test the boiler, just to make sure you have missed no additional tube leaks and the repairs are acceptable per the pressure testing requirements of the NBIC.

RE: how to seal a high pressure line for hydro

I agree conpletely with metengr - why do you want to do a hydro?  You should be able to get the results (check for leaks) with the test he suggested.  If you want to do a true hydro then you need to have those valves installed and in place to check for seal leaks on them also.

RE: how to seal a high pressure line for hydro

(OP)
Thanks for all the input, we ended up waiting for the valves, which by the way do leak themselves somewhat, so last tip was correct in that.  Not too much for what we are doing though, so full steam ahead.  Thanks to all.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources