Inrush Current
Inrush Current
Why is the magnetizing inrush current so high in transformers?
RE: Inrush Current
Vapplied = N1* d/dt(Phi)
= N1 * dPhi/di * di/dt.
When core enters saturation, we are on the saturated (flat) portion of Phi vs i curve where dPhi/di is very low. di/dt must become very large to compensate.
RE: Inrush Current
RE: Inrush Current
RE: Inrush Current
http://geocities.com/pschimpf/temporary_stuff/transformer_inrush_simulation.htm
RE: Inrush Current
RE: Inrush Current
RE: Inrush Current
The good old fashioned way to reduce the inrush current to the transformer, is a resistor in the circuit which is bypassed when the transformer is energized. The inrush current in theory also can be affected by the size of the iron core, the oversized iron core creates less inrush current (this is not a very economical solution either)
The inrush current affected by the following:
the size of the transformer, the resistance of the power system, the type of electric steel is used in the transformer, residual flux of the transformer, and which moment the transformer is energized (what is the residual flux and the system voltage relation at the switching moment).
RE: Inrush Current
RE: Inrush Current