plug welding broken anchor bolts

plug welding broken anchor bolts

plug welding broken anchor bolts

(OP)
I am the engineer on a project where the contractor broke off several anchor bolts at the top of leveling plate.  Is their a prequalified weld for using a "plug" weld for filling in the holes in the base plate which will sit on top of the leveling plate, to the top of the seared off anchor bolts?

RE: plug welding broken anchor bolts

I don't think that's considered a good solution, espcially if the anchor rods used are not weldable material.  Check out Thread725-105963

RE: plug welding broken anchor bolts

I tend to agree with UcfSE. Try AISC.org; their Steel Solutions Center provides guidance on this type of problem.

RE: plug welding broken anchor bolts

29 C.F.R. 1926.755(b)(1), which states that:
Anchor rods (anchor bolts) shall not be repaired, replaced or field modified without the approval of the project structural engineer of record.

A rod that is found to be fractured or does not meet required embedment lengths presents a serious condition. This critical connection between the post and foundation has been problematic.  In itself is not a serious deficiency as long as at least three quarters of the nut is engaged. If not, a coupler may have to be installed to lengthen the rod. This may involve complete foundation reconstruction. The first course of action is to see if the base plate can be lowered to fully engage the nuts.
One method of adding anchor rods is to drill through the base plate and into the foundation so that new rods can be epoxy grouted into place.  If epoxy bolts cannot be used, you might be forced to use a mechanical anchor.

Welding may be precluded if the anchor rod is not weldable. Determine what the carbon equivalence of the anchor rod is prior to welding. . Fracture critical material critical installations and fatigue induced loading may impact welding  Use the welding procedure for the anchors group of materials.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources