motor hand-auto selector switche
motor hand-auto selector switche
(OP)
Application is central air-handlers in a university building. Apparently some here want to specify that hand-off-auto selector switches be installed for fractional horsepower motors such as freeze-protection pumps (hot water air-handler coils) and electrical closet exhaust fans. My argument is that it's unecessary and the switch can be left in the off position accidentally and then freeze protection or exhausting of heat is defeated with possible repurcussions (I have experienced this actually). In general I strive to keep things simple and so I will argue against the extra "button" when not really needed. The arguement for it is that it eases maintenance troubleshooting and the added cost is minimal.
Anyone have any opionion on this?
Anyone have any opionion on this?





RE: motor hand-auto selector switche
I'm going to side with your techs. While it's true that a control can be left in an "off" condition, my experience is that it's far more common to need to manually force something "on" or "off" to correct a problem. Without an H-O-A, you either wire up a jumper (dangerous) or manually push a contactor button in (dangerous) or get a helper to make the start/stop happen from a remote control position (time consuming and frustrating).
If inadvertent disabling of freeze protection is an issue, they are available with locking provisions. I say spend the extra couple of bucks.
Good on ya,
Old Dave
RE: motor hand-auto selector switche
RE: motor hand-auto selector switche
It would also be possible to configure an alarm for "off and getting pretty cold", but seems more trouble than it's worth.
RE: motor hand-auto selector switche
Good point. I have a client hospital with 80 air handling units but only one guy in the building on evening and night shifts. We did one of those "off and getting pretty cold" alarms with a flow switch and low-limit in series for every one of the AHU's just so the lone fix-it-up-chappy could get a page from the DDC system if he were busy plunging a toilet or something when a freeze-protect pump died.
Most often, though, it's not worth the extra cost...
Old Dave
RE: motor hand-auto selector switche
RE: motor hand-auto selector switche
Same for the electrical closet, alarm to the DDC say when room temp rises above 90F or so.
RE: motor hand-auto selector switche