I'm looking for other's experience's with integral-vertical face and bypass steam preheat coils with respect to temperature overshoot when in 100% bypass mode.
I've got a new VIFB steam preheat coil in a brand new 100% outside air custom unit. When the outside air (OA) is above 40F, no problem, modulate the steam valve to get the 50F discharge air setpoint. Below 40F the dampers are modulated to get the 50F discharge temp. Problem is at 35F outside air temp, the dampers are in full bypass but the discharge air is 51F. This means that the air stream is picking up 16F with the dampers fully closed! There doesn't seem to be anything wrong with the steam valve or the dampers.
What have other folks seen for temp rise when the F&B dampers are in full bypass?
I'm looking for other's experience's with integral-vertical face and bypass steam preheat coils with respect to temperature overshoot when in 100% bypass mode.
I've got a new VIFB steam preheat coil in a brand new 100% outside air custom unit. When the outside air (OA) is above 40F, no problem, modulate the steam valve to get the 50F discharge air setpoint. Below 40F the dampers are modulated to get the 50F discharge temp. Problem is at 35F outside air temp, the dampers are in full bypass but the discharge air is 51F. This means that the air stream is picking up 16F with the dampers fully closed! There doesn't seem to be anything wrong with the steam valve or the dampers.
What have other folks seen for temp rise when the F&B dampers are in full bypass?





RE: VIFB Steam coils and temperature overshoot
If it's a 100% outdoor air system, just initiate F&B mode at 35°F and it shouldn't be a problem becuase you would have to provide that heating from the coil anyway. If it's a return system where the return air should be providing the heating, you maybe should dig deeper into the F&B operation. I would say a 3-7°F rise might be normal, not a 16°F rise... -CB
RE: VIFB Steam coils and temperature overshoot
I'm going to have the installation contractor do a "tightness test" on the dampers today.
-NEPE
RE: VIFB Steam coils and temperature overshoot
RE: VIFB Steam coils and temperature overshoot
I have been finding out that - no matter what - working with 30-35 F outside air (100%), there is no perfect solution. VIFB does work well for freeze protection, but I haven't had a lot of luck with temperature control with steam valve 100% open and dampers controlling outlet temp.
If you are using higher pressure steam (>15 psig) maybe try setting your valve open percentage something lower than 100%. You will be preventing modulation, the big issue with coil freezing, but the coil temp will go down a little bit.
I've tried this with some success.
I know this is remote, but any possibility of a steam leak?
RE: VIFB Steam coils and temperature overshoot
RE: VIFB Steam coils and temperature overshoot
Those coils work well for a couple years then performance tapers off.
I'm doing a 20,000 cfm system with one now.