I posted this in Electric Power Eng'r forum - no response:

We used a step-up voltage transformer for a test run with a variable-speed 60 Hz motor. There was an odd subsynchronous frequency near 9 Hz found in the converter output current signal. Could the frequency come from the step-up transformer?

RE: Step-up Transformer Frequency?

Was this converter an AC drive or some other device?

RE: Step-up Transformer Frequency?

(OP)
It's an LCI drive with a DC-link converter - we are thinking that the step-up transformer is affecting the electric circuit. Has anyone found that the effective resonance frequency could be as low as 8-9 Hz? This is a large motor with about 10 MW operated on a stable grid.

RE: Step-up Transformer Frequency?

Load Commutated Inverters and 10MW motors are out of my league.  Some else needs to deal with this.

RE: Step-up Transformer Frequency?

What's the configuration of the transformer? If the LCI is connected to the Y then the transformer should be left ungrounded (i.e the star point floating)to prevent harmonics.

RE: Step-up Transformer Frequency?

(OP)
I believe it is isolated WYE connection and has a secondary grounded connection. However, harmonics are not the issue - they were low - but there was the odd low-frequency 8 to 9 Hz.

RE: Step-up Transformer Frequency?

Could it be an interaction between the voltage control on the inverter and the load of the motor?  If there is a sudden change in conditions (eg motor switching on), the inverter compensates for added load, which affects motor maybe causing inverter to back off, so motor draws more current and so on back and forth.  A mechanical analogy would be trying to push and pull a lump of concrete using a long spring - you can get an oscillatory condition between the lump and the pusher.

Bung
Life is non-linear...

RE: Step-up Transformer Frequency?

(OP)
Perhaps it could be an interaction - the frequency was shown to be constant with motor operating speed. It likely is a natural frequency of the electrical circuit. Has anyone ever seen one that low - i.e. indicative of a long time constant?
See:
quinn.mech.uakron.edu/me340/notes/me340sum.ps

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources