Inverter Duty Motors
3

Inverter Duty Motors

Inverter Duty Motors

(OP)
Is there a difference between inverter duty motors and inverter capable motors?

RE: Inverter Duty Motors

I think there could be.  There are different aspects to using the motor with a VFD (putting operation at above rated speed to one side):
1.  the increased stress on the insulation because of high voltage transients (as a result of fast pulse rises times giving reflections at either end of the cable) - mitigated by using special enamel coatings for the winding etc.
2.  possibility of bearing currents - mitigated by insulated bearings etc.
3.  increased losses in the machine primarily due to current harmonics - mitigated by reducing the rating compared to a motor working direct on line.

You could say that a inverter-capable motor need only deal with 1. and 2., whilst the inverter-duty motor deals with all three.

RE: Inverter Duty Motors

2
There are no standards for these terms so you need to read the fine print in the specs carefully.  I've seen Inverter Duty, Inverter Rated, and Inverter Ready, all with no hint of what the term means.

Be careful.  The marketing people are running amok on these terms.

RE: Inverter Duty Motors

What DickDV said.  He gets a star.

RE: Inverter Duty Motors

DickDV, you are right of course.  It comes down again to which manufacturer you trust.

RE: Inverter Duty Motors

The only Spec. which really covers an inverter duty motor is IEEE841 spec, which is the Best Severe Duty motor, since their  is no legal definition or one by NEMA.  Standard EPACT motors may be used if the insulation is good enough to stand the spikes and transients, which may be produced by the drive, and if the runs are short in length.  Cooling is one of the factors, since the fan will turn at less RPM, giving less CFM of air movement to disipate the heat.  Also as was said earlier if one of the bearings is insulated, then there are no shaft currents to ruin the bearings.

RE: Inverter Duty Motors

NEMA MG-1 Part 31 deals with Definite Purpose Inverter Duty motors. When we specify motors, we use ask that the motor be built according to the standards of NEMA MG-1 Part 31 in an effort to quantify what we mean by inverter duty.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources