use of galvanised steel water pipe as connection material

use of galvanised steel water pipe as connection material

use of galvanised steel water pipe as connection material

(OP)
I have encounted the use of galvanised steel water pipe as a connection to a disconnector in a lv substation, has anyone had experience of this and knows a reference to calculate the current carrying capacity.

RE: use of galvanised steel water pipe as connection material

Galvanized steel water pipe is a good grounding electrode. However, there is concern regarding the loss of material by corrosion to maintain the galvanized pipe integrity for long time. An overside pipe (probably 3/4" or 1 ") may be OK.

Even though the following info is not for water pipe application, this guideline could be use for reference regarding ground rod useful service life as follow:


- 3.9 mil zinc coating: 10 years. (Not recommended for deep driving applications).
- 10 mil copper coating: 40 years. Acceptable for deep driving applications.
- 13 mil copper coating: 50 years. Recommended for deep driving application.


For additional details see the enclose site.

http://www.erico.com/products/GalvRods.asp


NOTE: If this project requires meeting the NEC, here is a quote applicable to galvanized solid steel rod:
Paragraph 250.52.A.5 of the 2002 issue of the NEC Code states that if a galvanized ground rod is to be used it must 1) be 0.625 inches in diameter minimum and 8 feet long or 2) listed! Since nearly all manufacturers of galvanized ground rods have produced to an old and outdated ANSI C135.30 document, the diameters have been well less than what the code mandates (other manufacturers have acknowledged that a diameter tolerance of +/- 1/32” has been considered acceptable).

RE: use of galvanised steel water pipe as connection material

(OP)
thanks for the response, I am familiar with the use of galvanised pipe for electrodes, but the issue I am dealing with is diiferent in that the piece of pipe is forming part of a continuous electrical circuit within a substation i.e. there is significant power flowing all of the time as opposed to in an earthing the electrode.
It is easy enough to get hold of conductor current capacity for copper or aluminium conductors, but I am not sure about steel, instinctively I think that it seems like a bad practice, but a utility is commonly using it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources