Hello,


I have two pieces of switchgear (same man.);

(1) The ground bus is mounted on metal angles spaced every couple of feet (cont. throughout unit).

(2) The ground bus on the next unit is bolted flat to the enclosure wall (cont. throughout unit).

Are there any electrical issues with laying groundbus directly on enclosure like this?

Regards,
TULUM

RE: Switchgear Ground

As far as I know, the Ground bus is always in direct contact with the enclosure for typical electrical equipment (except for an isolated ground).

Mike

RE: Switchgear Ground

(OP)

mpparent,

I guess my question came from the fact that in a control house (switchgear inside a building) there is a standard in the mines to provide a ground bus inside that is mounted on 600v insulators.

What is the advantage of this?  All the switchgear circuits are tied to this bus, however the switchgear circuits are also bonded to the building...

My only thoughts on both of these scenarios is the fact that theoretically the may produce a less resistive path fro ground current making it easier to monitor and keep at a safe potential.  

Shots in the dark...


Regards,
TULUM

RE: Switchgear Ground

Tulum,

What kind of switchgear? Metalclad? Seems the intention was a very simple form of busbar earth-fault protection  - by lightly insulating from earth all metal framework. The framework is connected to earth at only one point and a CT connected over this connection.

See:
http://www.areva-td.com/servlet/ContentServer?pagename=TDE/AGF_Product/Product_Detail&c=AGF_Product&cid=1089880316992&am%20p;rid=&lid=en&pid=1017999014820&tab=Chapters&id=1056536208254
Download Chapter 15 (Busbar protection) pg 236 (Ch 15.6)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources