Nozzle determination for Air Flow Test Chamber

Nozzle determination for Air Flow Test Chamber

Nozzle determination for Air Flow Test Chamber

(OP)
Hello,

Currently I'm designing a new measuring station to determine the air flow rate of an aircurtain.

In the standard 210 of AMCA Labroratory Methods of Testing Fans for Aerodynamic Performance Rating there are 3 different test methods that can work. These are Figure 11 Outlet Chamber Setup-Nozzle on End of Chamber and Figure 14 Inlet Chamber Setup-Ducted Nozzle on Chamber. And Figure 12 Outlet Chamber Setup-Multiple Nozzles in Chamber.
We like to choose for Figure 11 or 14 because they are excangeble.

The standard makes clear rules for the minimal velocity. Like under 5.3.2 Nozzles.
The average velocity at the nozzle discharge corresponding to the airflow rate at free delivery at the test speed is at least 14 [m/s]. But there are no clear limits for the maximum velocity other than a rule about settling means.

Is there anyone here having experience with testing according to the AMCA standard. Or has an idea what the velocity limit should be.

I need this do determine the range and number of nozzles I need to test air flow rates between 100 and 8500 cubic meters per hour.

Thanks in advance.

RE: Nozzle determination for Air Flow Test Chamber

From ASHRAE 41.2, Standard Methods for Laboratory Airflow Measurements:

Quote (ASHRAE 41.2, para 5.2.3.1):

The throat velocity of any nozzle in use shall not be less than 3,000 fpm (15 m/s), nor more than 7,000 fpm (35 m/s).

RE: Nozzle determination for Air Flow Test Chamber

(OP)
THX for the reply. Also found this on different sites.

Quote:

The nozzle selection is based on a differential pressure between 0.1 inches w.g. and 4.0 inches w.g. The lower limit (0.1 inches w.g.) is used to ensure the flow in the nozzle is fully turbulent and the higher limit (4.0 inches w.g.) is used so compressibility is not a factor (4.0 inches w.g. is approximately 1% of an atmosphere).

Currently I'm contacting AMCA about this. Because I don't have a clue how you should measure or determine the flow settling means.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources