NOT switching the neutral

NOT switching the neutral

NOT switching the neutral

(OP)
I have a 3000A grounded wye service with main breaker, GFP and 3 pole ATS.  The generator neutral and ground are not bonded together and are tied to the respective buses of the swithcboard.  Is this a code violation?

RE: NOT switching the neutral

No, this is perfectly legal.

RE: NOT switching the neutral

(OP)
So when running the plant on the generator, we have no GFP.  If the GFP trips the utility main, the generator will not sense normal power when restored.  Is this correct?  Do you see any other issues with this scenario?

RE: NOT switching the neutral

Ground fault protection will depend on the location of the ground fault detection versus the generator connections to the bus.  

The generator breaker can also have GFP.  

If your local 480 V main breaker trips, you should not be trying to re-energize from the generator, since you could be closing in to a bus fault.  You need sense loss of utility voltage ahead of the main breaker.  

RE: NOT switching the neutral

In your situation, where generator is not-separately grounded, the generator's neutral must be solidly connceted to the service neutral. Then 3P ATS is OK, and generator is also grounded (through the service neutral).

If the two neutrals are not interconnected (may be because the load does not need a neutral) then you must ground the generator neutral at the generator end.

RE: NOT switching the neutral

If you need GFP at the generator circuit breaker, you will need to install the neutral CT downstream of the ATS.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources