Grounding transformers
Someone knows how to calculate zig-zag reactor:
- Zero-qequence impedance
- Rated continuous neutral current
- grount-to-earth shortcircuit in systems with zig-zag reactor
RE: Grounding transformers
Long shot reference...
ANSI/IEEE Std C62.92.4-1991 …Application of Neutral Grounding in Electrical Utility Systems, Part IV—Distribution
   Annex A  Specifying a Zig-Zag Grounding Transformer
This standard busbar referenced is good.  Another standard you should review if you are specifying a grounding transformer is:
ANSI/IEEE Std 32 IEEE Standard Requirements, Terminology, and Test Procedure for Neutral Grounding Devices.
A good application reference, with examples, is:
"Neutral-Deriving Transformers for Grounding Low Voltage Systems with Delta-Connected Source Transformers," R. L. Smith, IEEE Transactions on Industry Applications, Vol. IA-18, No. 2, March/April 1982.
While you don't mention any interest in the associated protection schemes, I will also throw in
"Grounding Transformer Applications and Associated Protection Schemes", E. R, Detjen and K. R. Shah, IEEE Transactions on Industry Applications, Vol. 28, No. 4, July/August 1992.