Can the water flow to a condenser be varied?
The unit in question is approx 500 TR Centrifugal, Trane

I cannot find any Trane lit that covers this

RE: Condenser water flow

This one question has been most widely discussed among engineering community except chiller manufacturers. All the manufacturers recommend a constant flow through condensers.

Good luck,


RE: Condenser water flow

Trane's most recent engineers newsletter discusses design issues of the chiller/cooling tower system.  They make a good case for lowering the traditional 3 GPM per ton condenser water design flow, but they don't talk about variable condenser water flow.  See the following:

http://www.trane.com/commercial/library/vol34_1/ADMAPN014EN_0105.pdf

However, in the satellite broadcast of this subject last month, they did discuss low ambient temperature startup, for which one of the options was to reduce condenser water flow until the cooling tower water warms up.  This ensures that the chiller's refrigerant differential pressure doesn't drop to low, which can affect oil flow.  But this was on startup only.

Lowering condenser flow can cause problems in the tower, like reduced heat transfer between the water and air due to changed flow patterns.  You might want to look elsewhere for efficiency increases in the chiller/tower system, like variable condenser water temperature setpoint.

---KenRad

RE: Condenser water flow

Trying to control condenser flow ia bit like penny wise.......

You are better off keeping the discharge pressure low for that centrifugal compressor and the savings by doing that will be substantial.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources