(OP)
I am wondering what the opinions are out there of people who do this more for a living.  I know a service provider that needs high availability.  Because some site are unattended, they protect against UPS failure by putting an open transition, standard mechanical-transfer ATS on the output side of the UPS.  The critical load is a data center floor with lots of servers.

It seems to me that this replaces the single point of failure of the UPS with a non-maintainable single point of failure.  I don't think this is a good idea.

does anyone else believe in doing this?

RE: using ATS on output of UPS for bypass

Hi Eddie,

Many of the larger commercially-available systems have a static transfer switch (STS) to provide a no-break transfer from inverter to a bypass source. They may have an additional manual bypass in parallel with the STS to allow the unit to be shut down while continuing to provide power to the load, although clearly in this mode there is no UPS backup should the mains fail. All the preceding transfers do not need to cause interruption of power to the load.

There are installations which provide a 'disaster recovery' capability by which the entire UPS and transfer switch can be disconnected and power re-routed directly to the load. This can be done without interruption provided that the unit is already in its internal bypass mode. We provided this facility at our plant to allow supplies to be restored in the event of a total loss of our redundant UPS through, say, a fire within the UPS room. The switchgear is in a separate room.



----------------------------------

If we learn from our mistakes,
I'm getting a great education!

RE: using ATS on output of UPS for bypass

An open transition transfer switch is typically too slow to allow uniterrupted operation of the servers. You could use a closed transition ATS. I agree with your comment about the ATS being non-maintainable and another possible single point of failure.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources