High Volt. Pwr. vs Control systems

High Volt. Pwr. vs Control systems

High Volt. Pwr. vs Control systems

(OP)
I dont know am I posting in the right place or not, but I'm trying to find the effect of (if any) placing a 24 VDC control system in a station right under High voltage power transmission line (when I say High voltage I dont have figure, but I can tell you that if I'm standing under/close to the poles I can feel the magentic waves and hear that noise)

I know this question might looks incomplete but I'm trying to find different senarios for my situation.

RE: High Volt. Pwr. vs Control systems

If you can feel it, you have a valid concern for sure. The human body is a poor gauss meter, so if it is causing a sensation at all, it is likely very strong. Look into EMI (Electron Magnetic Interference) shielding for your enclosure(s) and be sure to use shielded cable.

"Venditori de oleum-vipera non vigere excordis populi"


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources