Sensitivity of temperature control vs. pressure control

Sensitivity of temperature control vs. pressure control

Sensitivity of temperature control vs. pressure control

(OP)
Hi, if I have one centrifugal compressor, and I would like to have the upstream control for the compressor speed, can anyone tell me that, is pressure transmitter or temperature transmitter more sensitive in term of response time? (the transmitters are both located on the suction scrubber of compressor)?
Thanks for everyone's input.

RE: Sensitivity of temperature control vs. pressure control

hi,

response time of temperature is longer than pressure.

regards

RE: Sensitivity of temperature control vs. pressure control

What is your control objective?  Are you trying to control the pressure upstream of the compressor, i.e. varying the compressor speed to adjust to a variable inlet flow keeping suction pressure constant?  Or do you have some other control objective?

RE: Sensitivity of temperature control vs. pressure control

(OP)
Hi 121202,
My objective is to achieve the process gas dew point at say, 5 degC @ 85 barg. In order to achieve this dew point specification, I would like to have compressor upstream pressure maintained at 60 barg, but with temperature control as the master to the pressure control, i.e. I am actually giving a cascade control, which the temprature controller shall override the pressure controller set point if the gas temperature set point is not met. I am wondering if this is a good control as I feel that temperature control may not be so sensitive. Thanks.

RE: Sensitivity of temperature control vs. pressure control

What you describe ("the temprature controller shall override the pressure controller") is not truly Cascade control, if you really mean Override. In cascade the temperature controller would be continuously sending a a set point to the pressure controller- override being an on/off term imho.
But assuming you do mean continuous Cascade:
You say "temperature control as the master to the pressure control", which correctly for cascade would work if the temperature moves slower than the pressure.
However you also say "My objective is to achieve the process gas dew point"
That suggest to me humidity control. Do measure humidity itself?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources