Lateral loads for Mezzanine?

Lateral loads for Mezzanine?

Lateral loads for Mezzanine?

(OP)
Other than seismic, what other lateral loads would you consider for a mezzanine? The mezzanine will be used as a gym with stationery bicycles and running pads.

RE: Lateral loads for Mezzanine?

I would not consider any other lateral loads, but I would check the floor system for vibration, if you are using concrete topping on steel deck on steel joists or beams.

DaveAtkins

RE: Lateral loads for Mezzanine?

You might want to design it for some nominal lateral loading.  Interior partition walls are typically designed for 5 psf.  That might be a good place to start.

RE: Lateral loads for Mezzanine?

I agree with Taro about using 5 psf lateral.  A small percent of the column load, say 1% or 2%, might also give you some kind of number to deign with.

RE: Lateral loads for Mezzanine?

In the UK, code requirements state you must allow a horizontal load of 0.5% minimum of the applied dead + imposed load acting simultaneously with gravity loads.

The purpose is to ensure a robust structure and allow for practical difficulties such as lack of fit and out of plumb.

The difficulty with assuming unit loads applied horizontally is that the floor system has a relatively low surface area which will attract little load.

RE: Lateral loads for Mezzanine?

I would only consider seismic. I would expect that to be larger than any other lateral load you can come up with. I also would check for vibration. Mezzanines can present a vibration problem.

RE: Lateral loads for Mezzanine?

For multi-storey buildings the Australian Standard AS4100 Steel structures specifies a notional horizontal force of 0.002 times the total design vertical loads at a floor level, applied at that floor level.  It is considered to act in conjunction with the dead and live loads for the strength and serviceability limit states.

The intent is to ensure a minimum resistance to lateral drift in both braced and unbraced frames.

Whilst your mezzanine floor is hardy a multi-storey building, the notional horizontal force is a sound principle for ensuring the robustness of the structure.

RE: Lateral loads for Mezzanine?

AS/NZS 1170.0, Structural design actions, has the following requirement for Robustness;
"6.2.2 Minimum resistance
The structure shall have a minimum lateral resistance equivalent to 2.5 percent of (G + ?cQ) for each level, applied simultaneously at each level for a given direction.
The direction of application of the lateral load shall be that which will produce the most critical action effect in the element under consideration, except that the application of this load in more than one direction simultaneously need not be considered in the design of any
element."
G = dead load, Q = live load, ?c = combination factor (=0.4 normally, 0.6 for storage etc.)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources