CANOPY WIND LOAD
CANOPY WIND LOAD
CANOPY WIND LOAD
Greetings; It seems that ASCE7-02 does not cover wind load in canopy trusses (i.e open building).  I am working on a steel canopy with cold formed trusses @4'-0" o.c. and spanning 60'-0".  If I use a tributary area of 4’x60’=240 sf   x (say 20 psf) =4,800# per truss which I believe is tooo conservative.  Any suggestions??, thanks..
1prsplmps1
RE: CANOPY WIND LOAD
For open buildings ASCE 7 only covers MWFRS pressures.
That being said, for a 60' truss at 4' o.c., 4800 lbs doesn't sound conservative to me at all, but I'm used to enclosed buildings.
UCFSE:  the 4,800# value may be OK for uplift forces but I think is high for horizontal force.
I agree, I understood what you wrote as being uplift.  That does sound high for lateral force.  Do they have a large vertical projected area?
UcfSE:  the trusses slope is 2:12 therefore 5.0 ft and the elevation at beam/truss bearing. = 30'-0”.  You can imagine how critical this height is for this design.  Thanks for your interest!!
1prsplmps1
If you are using the correct procedure for finding your forces by ASCE 7 then just use the numbers you get IMHO.  Even though that force seems large it is a 60-foot truss afterall.  Are you taking the wind pressure normal to the surface?
Yes, I guess I'll have to bite the bullet..