Quick Question- What would I read on a volt meter if I measured one leg to any building ground on an ungounded 3 phase delta 480 volt secondary??

RE: 3 phase delta voltage to ground

Somewhere between zero and 277 volts, depending on the capacitance to ground of the connected cables and equipment and on the input impedance of the meter.  Maybe more if the capacitance to ground is not balanced.

RE: 3 phase delta voltage to ground

If the delta system happens to have an earth fault, you will see ~480V on two legs, and ~0 on the earthed leg.

RE: 3 phase delta voltage to ground

By the way, make sure that your voltmeter has a decently high imput impedance (such as no less than 10 MegaOhms) and that your leads are fused, as you do not want your meter to become the 'second path to ground' on the delta system.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources