Synchronous Motor Capability per PF

Synchronous Motor Capability per PF

Synchronous Motor Capability per PF

(OP)
For example a large synchronous motor rated 14,000HP @ 0.85 leading PF.

What would be a good way to approximate maximum HP output at say 1.0 PF and 0.85 lagging PF?

RE: Synchronous Motor Capability per PF

Synchronous motors and lagging power factor? Some thing amiss!

RE: Synchronous Motor Capability per PF

Power factor can be adjusted on a sync machine by varying field excitaiton.

As a rough approximation, the power output limit is set by stator current heating (although there are other sources of heat that change with excitation as well and also other limits in the highly overexcited and underexcited regions).

In the case that stator current limit determines max power, the power output limit at 0.85 pf would be 85% of power output at 1.0 pf.

For sync generators, the supplier provides a capability curve.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.

RE: Synchronous Motor Capability per PF

On such a large machine the mechanical limitations of the machine at least need to be considered. 15% increase in output power is substantial.

Further to ePete's post, the heavily over-excited condition will probably be limited by the rotor reaching its thermal limit. In the severely under-excited condition, the stability limit of the machine will be reached. The stability limit will depend upon shaft loading. It is quite improbable that a motor would be operated at either of these extremes, so the limits are largely theoretical rather than likely to be encountered in operation.

There are a lot of similarities in the capability curves of synchronous motors and synchronous generators. Discussion of generator curves seems to be more common.

----------------------------------

If we learn from our mistakes,
I'm getting a great education!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources