Im using a 15 kva 440 vac pri. 400 vac sec. Y transformer in a 3 phase servo drive application do I need to be concerned about K factor?? Thanks in advance (trans center tapped to ground)
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Transformer
I would say that you probably do not have to worry. Especially if your servo is working intermittently and takes less than transformer rated current.
RE: Transformer
You did not mention is it an isolation transformer or just an auto transformer regulator.
If it is just an auto, this means the load is really large and posibility of harmonic generation in less likely but if if there is a seperate primary/secondary coils, all those have to go through the iron core and you may worry about harmonics generated.
Please note the difference between auto transformers and primary/secoundary transformers.
In auto most of the power pass directly from input to output and the transformer need to only compensate for difference, so with 440/400 volt rating you may actually need
(440-400)/440 or 1:11 th the power of a primary secondary transformer with the same voltage ratio