power factor correction

power factor correction

power factor correction

(OP)
I understand how and why power factor correction is used, but what I'm not sure of is what effect if any would there be for over correction?  (using a larger Capacitor load bank than is required)

RE: power factor correction

Using a larger capacitor bank than required will cause the power factor (p.f.) to become leading and is probably more undesireable than a lagging p.f.  Utilities usually don't want customers feeding VARS feeding into thier system.  

RE: power factor correction

Actually, sometimes we don't mind it, as it props up our voltage at the end of long feeders, but...

1) Most 'legacy' utility revenue meters cannot distinguish between leading and lagging power factors and will charge you for a poor power factor either way.

2) Some of your facilities equipment may not like the impact of excessive VAR's furnished by capacitors, as they tend to aggrivate the impact of harmonics and cause the voltage to rise above nominal levels.

RE: power factor correction

You must never "overcompensate" there is the resonance problem to deal with.

RE: power factor correction

Some switchgear (especially older stuff) doesn't particularly like switching capacitive current, either.

A lot of the old utility rules stem from it being easier to control something by having a blanket ban.  It is just too hard to deal with thousands of exceptions and how they might upset the system.  It's basically a paternal "greatest good of the greatest number" approach.  A lot of whiz-bang white-shoe entrepreneurial types hate it 'cos of their blinkered short term "it costs us money" approach to life!

Bung
Life is non-linear...

RE: power factor correction

(OP)
cbarn24050
What is the resonance problem that you spoke of? Would it not be present regardless of leading or lagging p.f.?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources