Need tips on motor upgrade
I'm a mechanical engineer working on a chilled water pump upgrade. Is there an expert willing to offer advice on the following? I have some old (1980 vintage) pumps that have 460/230V 50 hp motors running at full load, around 62 A. I would like to swap them out for slightly larger pumps which would require 60 hp motors to get the required flow. (I would load them to about 56 hp). According to my research so far, if I use premium efficiency motors (94%), the current should only be around 63 A.
So can I just install the new equipment without changing out the starters? The wire size to the motors is AWG 4 with 80A fuses. I don't know the rating on the overloads, they are obviously rated for the old 50 hp motors.
I have read that starting current on high efficiency motors is much higher than on old motors. Will I need a new, larger instantaneous overcurrent device? Some of the older starters don't appear to have an instantaneous device.
Thanks for any replies.
RE: Need tips on motor upgrade
As to your starter, only you can tell. Read the max. FLA on the starter label. THAT is the only determining factor. HP labels are essentially a guide.
"Venditori de oleum-vipera non vigere excordis populi"