star/delta motor starting

star/delta motor starting

star/delta motor starting

(OP)
In star/delta motor starting the line contactor(i.e. the contactor other than start(which connects the winding in  star) contactor and run(which connects the winding in delta) contactor)  is connected inside the delta connection. This contactor can also be connected outside the delta connection. I just want to check that the reason for connecting it inside the delta is to break lower current or anything else.    

RE: star/delta motor starting

That contactor can not be outside of the delta because it has two functions: a) connect to the power lines, b) Make the motor winding delta connection. (i.e. connect terminal 1 and terminal 6 together.). Note that motor terminal 1 remains connected to the power line since the start condition.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources