Check Valve for Low Pressure
Check Valve for Low Pressure
(OP)
I am looking for a 12" check valve for Methane at low pressure. Pressure of line is 8" Water column. It is a Biogas installation.
Any idea???
Any idea???
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Check Valve for Low Pressure
|
RE: Check Valve for Low Pressure
Mike Halloran
NOT speaking for
DeAngelo Marine Exhaust Inc.
Ft. Lauderdale, FL, USA
RE: Check Valve for Low Pressure
RE: Check Valve for Low Pressure
FransiscoG, what are you planning for the check valve to do? Could the task be accomplished with a compressor-discharge check? Any swing check will require something on the order of 6" H2O to open, and in a 12" pipe it is probably more. Your stream doesn't have any extra energy to waste in operating a check valve unless it is crucial to the operation.
David Simpson, PE
MuleShoe Engineering
www.muleshoe-eng.com
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips Fora.
The Plural of "anecdote" is not "data"
RE: Check Valve for Low Pressure
RE: Check Valve for Low Pressure
Companies like Groth, Protectoseal, and Varec make low pressure vents that start opening at around 1/2 ounce/in2. AN inline vent might be your best bet for a mechanical valve.
RE: Check Valve for Low Pressure
Imagine a lift check valve, the kind you make from barstock. Ports on either end, coaxial. Communicating holes toward the center, one drilled up, one drilled down.
At the center, a blind hole drilled from the top to intersect the lower communicating hole, and a counterbore at the top, intersecting the upper communicating hole. Ordinarily, you'd put a lifting poppet and maybe a spring in the counterbore, then cap it. Forget the poppet. Forget the spring. Just cap the body.
Now, invert it, and fill the counterbore with water.
Gas flowing in the forward direction of the former lift check valve depresses the water level and bubbles out to the discharge port.
Gas flowing in the reverse direction tries to do the same thing, but can't lift the water in the deep vertical drilled hole, because there isn't enough pressure to lift the water that far.
Ergo, check valve, with no moving parts other than the gas and the water.
You might have to replenish the water.
Mike Halloran
NOT speaking for
DeAngelo Marine Exhaust Inc.
Ft. Lauderdale, FL, USA