PF Correction

PF Correction

PF Correction

(OP)
We're interested in eliminating the losses in our distribution system that are created by reactive (and harmonic) currents.  Fortunately or unfortunately as the case may be, fixed capacitors were installed some time ago at our main service entrance to eliminate/minimize the power factor penalty from the utility company.  That's proven effective in eliminating the penalty and fixing the utility's problem, but we'd still like to reduce our "inside" losses.  Are there any concerns with installing static capacitance AT our 480 VAC inductive motor loads to further cancel out the inductive current and reduce our losses?  Thanks in advance for the feedback.

RE: PF Correction

Adding capacitors can have negative interactions with system harmonics, therefore a deep power quality study is recommended.

RE: PF Correction

See Thread237-112076

I do not know how large you faciltiy is. It would have been better had you had installed the caps at the motors to begin with in place of adding fixed caps. I assume your fixed caps are at the service entrance or the main board.

Reduction in I2R losses alone seldom justifies buying and installing new PFCs.


RE: PF Correction


Large plants use them but to correct for losses within the confines of your plant would be hardly justifiable

RE: PF Correction

Also you do not want to install "more" capacitors then what you already have, if the existing pf is above 0.9 or so. Watch for over correcting.  It is another matter if you want to move them to a different location in your facility.

To maintain the sam e pf, if you add new ones at the motors you may have to remove some from the 'fixed' bank.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources