I have a RSView32 project running on a Windows 2000 workstation. Occasionly the RSView project will stop communicating with the PLC. I will view my communication driver settings, and it will say that my primary communications driver is "none loaded". I will reconfigure the driver, and it works fine. My PLC is a SLC 5/04, communicating on DH+ with a KTX card in the PC. Anyone else had this problem? Know of a solution?
Thanks
Thanks





RE: RSView Communication Driver
RE: RSView Communication Driver
RE: RSView Communication Driver
Good Luck!
RE: RSView Communication Driver
You did not mention the series of PLC, but here is the problem I ran into. The Panelview Plus was designed to talk to the Control Logix platform. If you are using a SLC or Micrologix, it's hit or miss. Also, it wasn't really designed for serial DH485 either. If you are talking to a SLC or Micrologix, either use full duplex DF1 or Ethernet.
The Rockwell guys got a bit ahead of themselves (in my opinion) and the software is full of bugs. I made the mistake of uninstalling in the wrong order and tech support had me deleting registry information so I could fully remove it before installing the next version.
RE: RSView Communication Driver
RE: RSView Communication Driver
RE: RSView Communication Driver
Try configuring RsLinx to run as a service on your machine. This should solve your problem.
RE: RSView Communication Driver
RE: RSView Communication Driver
In your orginal posting you stated "I will reconfigure the driver, and it works fine". What exactly do you do? Do you open up RsLinx? Another possibility is that RsView is not correctly stating up RsLinx or waiting for the RsLinx service to start. Two ways to correct this. Try to un-install RsView and re-install. The other is to get into RegEdit and play around with the service dependencies (not recommended).
RE: RSView Communication Driver
RE: RSView Communication Driver
Check to see if RsLinx is running before and after your go into RsView. Another way to check is when this event happens again, shutdown RsView. Make sure that RsLinx is running, and then start up RsView. If it works, then you know that RsView is not starting up RsLinx, or is not waiting for it to completely start.
RE: RSView Communication Driver
I copied this example from the help file for the object browser in VBA. It is located at RSView32.Channel.PrimaryDriver within the object browser. Hopefully this will lead you in the right direction. Good Luck!
Sub Channel_Define()
Dim oChannel As Channel
'Get a reference to Channel 4
Set oChannel = gChannels(roChannel4)
'Configure the Channel
oChannel.NetworkType = "TCP/IP"
oChannel.Messages = 3
oChannel.PrimaryDriver = "AB_ETH-1"
oChannel.SecondaryDriver = ""
oChannel.ActiveDriver = roActiveDriverPrimary
'Write the configuration
oChannel.WriteConfiguration
'Release resources associated with the object
Set oChannel = Nothing
End Sub