Indoor /Outdoor Resets

Indoor /Outdoor Resets

Indoor /Outdoor Resets

(OP)
Looking for the best way to compute energy savings from adding indoor outdoor resets to boilers.

RE: Indoor /Outdoor Resets

Do bin data analysis where temperature occurance is given in 93) 8 hour blocks of daily data. See NAVFAC MILITARY Weather Data Tables. Do (2) sets, one with reset, one without. Total up Btu for each temperature bin = Design Btuh load x count of hrs x (ti-to actual)/(ti-to design).

Take the total Btu difference between w/ & w/o rest.

Say average efficiency = 80% so Btu fuel input saved = Btu saved /0.8

Determine cost of fuel saved.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources