can i use gate valves for isolating a PCV used in a natural gas line?

RE: gate valves for control sets on gas lines

Define isolate? If bubble tight isolation is required, the answer is probably not.

RE: gate valves for control sets on gas lines

If it is a big line, then the operators will hate you, if it is a small line, then why bother (small ball valves and small gate valves are about the same price).

David Simpson, PE
MuleShoe Engineering
www.muleshoe-eng.com
Please see FAQ731-376 for tips on how to make the best use of Eng-Tips Fora.

The Plural of "anecdote" is not "data"

RE: gate valves for control sets on gas lines

(OP)
zdas04

you are very funny. it is an 8 inch line and is the outlet from a oil-gas separator. the isolating valves are part of the PSV's control set. i dont know whether a gate valve can be tightly sealed or not.

thanks farzin.

RE: gate valves for control sets on gas lines

Actually, I wasn't trying to be funny.  I once installed a 12-inch gate valve in a valve-can on a gathering system.  The valve takes almost 100 turns to operate, and the linkage from the handwheel to the top of the can is not as well aligned as I would have hoped.  For a while we were cycling it once a week to run pigs - I got hate mail.

If an 8-inch gate valve ever completely seals, it is a coincidence.  They are not made for a bubble-tight seal and I would never consider one for an isolation under a PSV.

David

RE: gate valves for control sets on gas lines

(OP)
thanks david, I will remember your advice.

RE: gate valves for control sets on gas lines

We use gates for PSV, PCV, control valve loops, pumps, compressors...isolation period, all the time to great success.  Location is 30,000 BPD crude unit and 10,000 BPD high pressure hydrotreater.

Use a reputable manufacture such as Crane, Velan, Powell, Bonne Forge and you'll be fine as long as the metalurgy matches the service.

If the service is high pressure and you really want to get as close to 100% isolation as reasonably feasible, then spec out an Orbit Valve.  http://www.coopercameron.com/cgi-bin/ccvalve/products/productdetail.cfm?OID=15661732&pageid=ccvbrands&thismenu=menu6

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources