AWWA D-115 states "The maximum center-to-center spacing of circumferential tendons shall not exceed three times the wall thickness, unless an elastic analysis is made for the effects of the greater spacing".  I have a situation where I will need to exceed three times the wall thickness (somewhere around 4.5).  What exactly does the code mean by elastic analysis.  Do I simply need to check the deflection and design flexural steel for the concrete spanning vertically between the tendons or is there something more involved that needs to be considered?

Also, is it sufficient to perform the check with static fluid pressures or do impulsive and dynamic seismic forces need to be considered as well?

One more thing, if any one knows of some good reference material on this topic I would appreciate some recommendations.

Thanks,

RE: AWWA D-115 Prestressed Tank Question

It sounds like they want you to use shell theory to confirm proper prestress in between the tendons.  The shell would tend to bulge out slightly there.  I believe this would normally be based on static pressures, not seismic loads.

"Formulas for Stress and Strain" has various cylindrical shell formulas that would probably cover the case.

RE: AWWA D-115 Prestressed Tank Question

I'm confused.  There are a very limited number of companies that install prestressed tanks.  They mostly do there own designs.  If you don't work for a prestressed tank company why are you doing the design?  And besides that, why exceed the spacing recommended by the code?

RE: AWWA D-115 Prestressed Tank Question

Jed, maybe he does work for a tank company.  Anyway, it's a reasonable question, figured we'd see some other answers.

RE: AWWA D-115 Prestressed Tank Question

(OP)
Yes, JStephen is right.  I do work for a young prestressed company.  Up until now we have always met this criteria but now we have a situation where a large penetration will force our strand spacing past this limit and sweeping will only get us so far.
Anyway, good idea JStephen, I will check my Roarks.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources