Prestress I-Beam Girder w/raised concrete median load
3

Prestress I-Beam Girder w/raised concrete median load

Prestress I-Beam Girder w/raised concrete median load

(OP)
I am looking at the AASHTO Standard Specs Section 3.23.2.3.1.3 for design of a Prestress I beam girder type IV.  I am looking at an interior beam carrying some of the load of a raised concrete median.  I have always thought of a raised median and a sidewalk as being similar (concrete load on the composite section), except for the sidewalk LL provisions.  My question is why is an exterior beam carrying a sidewalk LL designed as per AASHTO standard Specs 3.23.2.3.1.3,overstress allowed at 125%. But no similar criteria for interior beams?  Any guidance would be appreciated.

RE: Prestress I-Beam Girder w/raised concrete median load

My interpretation of that part of AASHTO is as follows:

1.  All composite dead loads (railing, sidewalks, wearing surfaces, raised medians, etc.) get evenly distributed among al of the beams per AASHTO 3.23.2.3.1.1.

2.  Sidewalk live load assumed to be carried by the exterior girders.  This is the part I'm not exactly sure of.  I have sometimes also distributed sidewalk live load among all of the beams and ignored the 25% allowable stress increase.

3.  If you assume that the sidewalk live load is carried by the exterior girders only, you can increase the allowable stress by 25% for the condition of sidewalk live load and traffic live load acting on this beam.

4.  If for some reason the sidewalk was down the center of the bridge, I think this provision could be applied to an interior girder.

Hope this helps.

RE: Prestress I-Beam Girder w/raised concrete median load

Typically exterior beam would carry both highway (truck) loads, and pedestrian loads. Probability, that both (or even the full pedestrian load) would occur simultaneously is very low, so designing the girder for these loads is very conservative. In some cases (mountable curb, or lack of barrier separating vehicular load from sidewalk) the girder should be checked for full truck loading, with 125% overstress provision.

RE: Prestress I-Beam Girder w/raised concrete median load

I agree with both posts as noted above.  My design experience follows exactly with what broekie has noted.

Regards,
Qshake

Eng-Tips Forums:Real Solutions for Real Problems Really Quick.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources