Tension rod sag
Tension rod sag
We have some big cantilevered architectural canopy, where we have 1-1/2" diameter tension rods splaying out from a vertical column (similar to a cable stay bridge). Well, the rod that goes to the end of the canopy is about 31' long at a 45 degree angled slope, doing a beam deflection calculation (for beam on a slope) gives a deflection of 12.8" just under its own weight.
This sag seems too excessive . . . is there any problem with using a tension rod with this much sag in it? The roof of the canopy is going to be poured concrete. I am just having trouble envisioning this rod with that much of a deflection. It would seem like it would start straightening out when they start pouring concrete on the roof and that it would be impossible to get the roof set level and at correct elevation.
We will take a long time to look at this, so I am just posing this question to see if someone has come across this situation before, and if my fears are founded in how the sag would affect the construction of the roof.
On a side note: I've been asking a lot of questions lately, so thank you to everybody who has taken the time to respond to me. I've been getting into a lot of "one of a kind" and "new to me" type projects, and also find out that a lot of them are new to my bosses as well. Just running things by you fine folks on the more difficult issues.
RE: Tension rod sag
How are your axial deflections working out for you? Will the rod stretch much and cause the roof to sag down? Are these rods exposed to wind? You might have some vibration problems or encounter some vortex shedding from the wind. Rain water on the cables may also exacerbate the problem by increasing drag. I believe AISC recommends limiting tension only members to a KL/r of 300 to help with these issues.
Can you add some sort of adjustable device such as a turnbuckle? I'd bet the architect wouldn't like that though.
Is the roof of a shape such that ponding stability could be a problem, or is it sloped or drained well?
These are some things that come to mind. I don't have any "real world" experience with a structure like this to be able to give you some real advice. It sounds very interesting, let us know how it goes
RE: Tension rod sag
You might however also want to look at things like Icing, creep and reversal due to wind as well as vibration and harmonics which can be a problem for tension structures. You should also seriously consider inspection and maintenance which I think are often overlooked by Architects on low budget stuff.
RE: Tension rod sag
You can not treat it as a simple beam, you have to model it using any design software.
RE: Tension rod sag
Ciao.
RE: Tension rod sag
A couple of points:
1) The code says: "For members in which the design is based on tension, the slenderness ratio for l/r preferably should not exceed 300. The above limitation does not apply to rods in tension." We had a 1-1/2" diameter solid rod and were taking this exception to make this work. Is there any problem with using this exception?
2) Using RISA 3D, the tension rod, even as marked as a tension only member, showed this 12" deflection and a bending moment. I'll have to read up with RISA 3D to see how to model those members as actual cables. Any thoughts?
3) As for the canopy itself, we have steel framing supporting concrete deck spanning between the steel members. It is sloped and drained well; since the framing is all steel, creep won't be a problem; and we have provided enough dead load with the concrete roof, to counteract the straight wind uplift on the canopy. What I am not too sure about is if anybody has looked at the more dynamic aspects of the wind loading, such as vibration of those tension rods (I'm just started reviewing this canopy designed by others in the office, so I've only looked at it for a day). That is something I'll have to check into.
By the way, this canopy is on a building, about 650 sf, and the roof is about 13.5' tall. This is a pretty low budget (construction wise, anyways) canopy.
RE: Tension rod sag
RE: Tension rod sag
I may argue that your rod is not only in tension but with bending as well. So you are not complying the code to the letter. I will interpret the code to mean vertical rods for lifting purposes.
Ciao.
RE: Tension rod sag
RE: Tension rod sag
Good luck.
RE: Tension rod sag
A 1.5" diameter rod 31 feet long has a kl/r near 1000. I would expect this to be highly sensitive to dynamic effects from wind. It's going to require a much more involved analysis than just sizing rods for static loading. Limiting the slenderness ratio helps alleviate problems you can get with such slender members, though the limit is of course not required.
As you see you have to be a little careful how you model things in software. RISA uses beam elements for everything (except plates of course). Checking the T/C box does not change the element to a bar type but rather only reduces or eliminates its ability to carry load in a certain direction. This is a great example demonstrating that you have to be aware of what the software is doing. You can get any answer you want but that doesn't make it right
RE: Tension rod sag
Next, I would calculate a wind load then apply a multiplier to it to account for vibration.(similar to multipliers for the number of expected cycles for a crane)Calculate the bending stress then add to the previously calculated tensile stresses for a maximum tesile stress in the rod. Make sure your rod is amply sized.
If possible, you might consider a tube shape to stiffen the element as a 1.1/2"Ø rod is quite a chunk of steel. But then the kl/r may become an issue.
For an easy non-intrusive adjustment mechanism with your rod set at a 45° angle, thread the rod and set it through the column and an equal angle leg.
(this type configuration)
In retrospect, it seems for a low cost job this is a mighty elaborate design. columns at the ends would be a much more cost effective solution.
RE: Tension rod sag
Your opinion to DELl2000 about tension rods only being used in a vertical orientation for lifting purposes seems like quite a limiting opionion on the use of tension rods. I think the code relaxation of kL/r limits for tension rods is also based on assumption that the tightness of the rod can be controlled somewhat by the use of a turnbuckle. This helps prevent problems like fluttering in the wind. If you look at the (possibly millions) of sway rods used for elevated water tank construction you will note that the code use of tension rods is not limited to rods in a vertcal orientation only.
Steve Braune
Tank Industry Consultants
www.tankindustry.com
RE: Tension rod sag
We have met this problem of the RISA Beam theory (its not only RISA by the way but most all software) and excessive sagging rods in the output. What you can do is set up a fictional material property that matches the steel properties except that you set the density to a very low number (0.00001) and assign that to the rods. The sagging most likely came from the self-weight (-1) in your basic load tables for the Y direction. You can still use this but with the low density assigned to the rods they won't deflect much at all - basically you are "fooling" the computer to ignore the sagging as it will actually be taken up by the tension in the rod. Do add joint loads at each end of the rods to make up the lost rod weight so it is still included in your model.
Now the dynamic concerns above - you still need to check those.
RE: Tension rod sag
RE: Tension rod sag
I would consider either havig a turnbukle or theaded end to allow for adjustment of the roof when you are done. If you do use threaded ends, check to see if the ends should be upset.
RE: Tension rod sag
Rods do sag... often several inches. Go look at your mother's or grandmother' clothes line. Turnbuckles will indeed lessen the sag, but not eliminate it.
LPPE.
31 foot rods are not really all that long. Elevated water tank tower rods are usually in the the 50 ft to 70 ft range. Good comment about the upset of the turnbuckle ends. That's sometimes overlooked.
Steve Braune